🏡 Better Homes OffshoreDrilling's (mostly) DIY Solar install extravaganza.

Thread
Why Solar?
Economics of Solar

LikeABauce302

TCG Elite Member
Aug 27, 2013
5,926
16,513
South suburbs
Real Name
Matt
Finally caught up on this thread. This is awesome. I love seeing DIY projects, especially bigger ones like this where you're figuring everything out as you go along.

One thing I absolutely hate when I'm taking on a new project is when someone asks me if I know what I'm doing or even worse tells me I need to hire someone because I don't know what I'm doing. Even if I was still on the fence about the project, that's when I decide that I'm absolutely going to get it done by myself, no matter what kind of OSHA violations I will make :LOL:
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
Whats the cost on the panels?
I’m $18,426 into the project so far. That’s permits, engineering, lumber, upgrades to attic to make it easier to work, tools I didn’t have, all the solar parts.

I have some wire but not enough to do the whole project. Expecting to be just under $19,000 when I’m done
 

Jimy Bilmo

CSVT OG Member
TCG Premium
TCG Goldmember
Aug 16, 2005
39,070
61,378
I’m $18,426 into the project so far. That’s permits, engineering, lumber, upgrades to attic to make it easier to work, tools I didn’t have, all the solar parts.

I have some wire but not enough to do the whole project. Expecting to be just under $19,000 when I’m done
Did you ever get a conventional quote?
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
Finally caught up on this thread. This is awesome. I love seeing DIY projects, especially bigger ones like this where you're figuring everything out as you go along.

One thing I absolutely hate when I'm taking on a new project is when someone asks me if I know what I'm doing or even worse tells me I need to hire someone because I don't know what I'm doing. Even if I was still on the fence about the project, that's when I decide that I'm absolutely going to get it done by myself, no matter what kind of OSHA violations I will make :LOL:
If you have any aptitude in the trades most things are easy enough to google and YouTube what specific knowledge you need.

I don’t know if it was this thread that I said it, but if there’s something I can do myself for cheaper than hiring it out, I get to buy new tools to do it and I have a chance to learn something, I love to do it.
Did you ever get a conventional quote?
$46k for the equivalent system. Without any of the structural work I did.
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
Solar wholesale.

They’ve been fucking HORRIBLE on communication. Like 5 emails and phone calls with voicemails and no response. Had to go through their new customer question form to get someone to respond to me. Once I got past the design phase communication got better. I don’t know if it was the person I dealt with or what.

If I was going to do it again I’d go with someone else. Oh well!
 

JBruno88

TCG Elite Member
Apr 3, 2014
1,454
955
Carol Stream, IL
I’m $18,426 into the project so far. That’s permits, engineering, lumber, upgrades to attic to make it easier to work, tools I didn’t have, all the solar parts.

I have some wire but not enough to do the whole project. Expecting to be just under $19,000 when I’m done

What’s ROI Looking like? $19k up front cost, what are you planning to save on electricity monthly and what are you looking to sell back to ComEd? I’d be really curious to see how many months till you “break even” and start putting money back in your pocket vs the warranty period on the panels and components.
 

Jimy Bilmo

CSVT OG Member
TCG Premium
TCG Goldmember
Aug 16, 2005
39,070
61,378
What’s ROI Looking like? $19k up front cost, what are you planning to save on electricity monthly and what are you looking to sell back to ComEd? I’d be really curious to see how many months till you “break even” and start putting money back in your pocket vs the warranty period on the panels and components.
If my bill was $300/mo, as it's usually around there, it'd take me 64 months to break even, without them giving money back for power back to the grid. Seems well worth it IMO.
 
  • Like
Reactions: frank and Aircal

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
My system is estimated to produce 11428 kWh/yr and ComEd cuts you a check for 15yrs of production. Each SREC s for 1 MWh of production.
So 171.42 SREC at the current rate of $82.48

I should get a check for $14,104.44 from ComEd and my outstanding balance is $13,300

I’ll be paid $804.44 to install them all said and done.
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
My system is estimated to produce 11428 kWh/yr and ComEd cuts you a check for 15yrs of production. Each SREC s for 1 MWh of production.
So 171.42 SREC at the current rate of $82.48

I should get a check for $14,104.44 from ComEd and my outstanding balance is $13,300

I’ll be paid $804.44 to install them all said and done.
Oh, this counts as income so whatever tax bracket that’s in too.
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
Are there other cons to feeding back into Comed other than the extra equipment to prevent back feeding and permitting?
I really don’t anticipate any. You’re at the mercy of the grid being up for your solar to be online unless you have batteries, that’s it. My power is reliable so that’s not an issue. Power flashing off a couple times a year during storms isn’t worth the 5-6 figure price of batteries.
 

Lord Tin Foilhat

TCG Conspiracy Lead Investigator
TCG Premium
Jul 8, 2007
60,728
56,890
Privy Chamber
I really don’t anticipate any. You’re at the mercy of the grid being up for your solar to be online unless you have batteries, that’s it. My power is reliable so that’s not an issue. Power flashing off a couple times a year during storms isn’t worth the 5-6 figure price of batteries.
ahhh gotcha. I thought you also had some sort of onsite reserve.
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
Bent my last piece of conduit between taking care of the baby today. 160’ of 3/4” EMT and only turned one piece into an art project :bowrofl:

I’m going to keep knocking out little bits when I can today and tomorrow. Monday should be plenty of time to get wire pulled and things completed enough to be ready for inspection.
 

OffshoreDrilling

This is my safe space
TCG Sponsor
TCG Premium
HVAC Guy
Aug 28, 2007
39,237
50,925
Homer Glen
Annnnd we done. Done enough to call for an inspection at least. Can’t believe I finished this crap and it snows today :bowrofl:

I got all my wire pulled yesterday, terminations made at the roof junction boxes to the arrays, combiner panel and disconnect mounted on the wall and put my warning stickers in the wrong spots.

There are a couple tiny things left to do before the inspector shows up. I need to make a panel schedule and hang smoke detectors in every room upstairs. Who the hell knows when I’m going to have time to throw drywall up .

Once it passes inspection or i correct what doesn’t pass, i can submit my signed inspection form to ComEd then wait for permission to operate PTO.


Here are some uninteresting pictures of conduit and wires:

3BBFB548-1958-456D-9819-380DC5119ADF.jpeg
House roof into attic, it cuts to the right and down through top plate and the wall of my master bedroom.
FA9B5BC4-8201-4348-988E-681C4522585B.jpeg
From the nester bedroom wall across the garage rafters along the knee wall that frames out my balcony.
A2B351BD-0420-489E-9F0B-EF61451D4FBF.jpeg
This is the garage roof, tees into a box with conduit from the stuff that came from the house roof then down the garage wall.
B57AC649-6A47-4D63-9EFC-6D8A83642735.jpeg
Conduit from garage attic goes down the wall here and into the crawl in my basement, then a straight 50’ shot across to my breaker panel.
8E37542E-88FB-4671-8617-C4E25F6056F0.jpeg
Borrowed the megafuck MX Fuel core drill from work to pop a 1.5” hole through the brick veneer into the basement.
1251CB82-FED1-4B65-9AA0-016B0CFD91A7.jpeg
Disconnect and combiner panel. Squeezing 5 #10s and 3 #8s into a 3/4 conduit was not fun.

264A8B97-3698-40E7-AB62-0D5A985370D9.jpeg
One of the roof junction boxes.


THE END?

9BD79ECD-871C-4FB0-AB67-6996CDFB249E.jpeg


7D433795-74CF-406A-895D-C91AF7D88E22.jpeg


3506F542-9A58-4E51-83BE-A9A786F6B688.jpeg


42ED2DF2-4D5E-41B4-AAB8-400624D680B1.jpeg


5FDBCEF4-0AEA-4AC4-81EE-E0C93EC9F288.jpeg


35E84A1E-7E1D-4B2C-96A4-E4E993097B43.jpeg
 

FESTER665

TCG Elite Member
TCG Premium
Apr 13, 2008
40,165
66,676
Streamwood
Annnnd we done. Done enough to call for an inspection at least. Can’t believe I finished this crap and it snows today :bowrofl:

I got all my wire pulled yesterday, terminations made at the roof junction boxes to the arrays, combiner panel and disconnect mounted on the wall and put my warning stickers in the wrong spots.

There are a couple tiny things left to do before the inspector shows up. I need to make a panel schedule and hang smoke detectors in every room upstairs. Who the hell knows when I’m going to have time to throw drywall up .

Once it passes inspection or i correct what doesn’t pass, i can submit my signed inspection form to ComEd then wait for permission to operate PTO.


Here are some uninteresting pictures of conduit and wires:

View attachment 139493
House roof into attic, it cuts to the right and down through top plate and the wall of my master bedroom.
View attachment 139495
From the nester bedroom wall across the garage rafters along the knee wall that frames out my balcony.
View attachment 139492
This is the garage roof, tees into a box with conduit from the stuff that came from the house roof then down the garage wall.
View attachment 139496
Conduit from garage attic goes down the wall here and into the crawl in my basement, then a straight 50’ shot across to my breaker panel.
View attachment 139497
Borrowed the megafuck MX Fuel core drill from work to pop a 1.5” hole through the brick veneer into the basement.
View attachment 139499
Disconnect and combiner panel. Squeezing 5 #10s and 3 #8s into a 3/4 conduit was not fun.

View attachment 139503
One of the roof junction boxes.


THE END?

View attachment 139494

View attachment 139498

View attachment 139500

View attachment 139501

View attachment 139502

View attachment 139504
Love those WAGO connectors.... Even use them on the low voltage landscape lighting that I just did, was worth the little extra cost....
1668520449057.png
 